Size the OCPD as per 430-52 & table 430-248: 17A x 2.50 = 42.5, use a 40A breaker and #8 THHN cu branch conductors 310-15, (building wire not NM or SE, these will need to comply with 334-80 & 310-15), the equipment grounding conductor is sized as per 250-122.